OPCUA plc input script don´t write to server opcua and plc
Hello
I have managed to connect opcua4unity with the kepware server.
opcua4unity <-> kepserver <-> cp1l(omron) and opcwatch.
opcwatch connects perfectly with kepserver, reads and writes without problems.
opcua4unity connect ok, import nodes ok and read ok, but don't write values to server and plc.
attached photos.
I have also tried write value=on and subscribe value=off, but it doesn't work either.
Thank you.
Antwort
What I am wondering about is, that you are subscribing for the value. You should only subscribe for Outputs. Please try in changing this and maybe if it still does not works please do a test setup where you try only one Input.
Maybe one more reason is, that you are not able to write to physical available PLC inputs. If the (real) input (where the wire is connected to) is low - you might not be able to put it to a high. Maybe you need to write into a PLC area where no "real" inputs are defined. But this is just a guess - we don't know Omron.
Best regards
Thomas
the area "D" where try to write is a memory area and not physical channel.
I also tried without subscribing and it doesn't work either.
I have tried to write booleans in the memories of brands of omron plc and it does not work either.
but all this can be written from opcwatch.
Best regards
Edu
Hi, currently I don't know where the problem is. On our side the test models with writing signals to an OPCUA server are working. Maybe there is something special with your OPCUA server but I have no clue where your problem is. We can't test it here on our side because we have no Omron PLC. And as I can see there is also no error message in the console log. Do you see any chance that we can get a connection to your OPCUA server. Maybe via a temporary VPN like ZeroTier?
in the photo I sent from unity the console notice says that I have to disable subscribe value.
I've tried it but it doesn't work either, although the warning no longer appears.
I have done tests with the kepserver simulator
without the omron plc, only with one node and with the same result.
between clients such as opcwatch or uaexpert being both connected if they can write and see the value updated on the other.
It seems fine to me to make a connection with zero tier or anydesk.
Thank you.
Hi, I am today (european time) one day off but will work today evening and Saturday evening. Can you setup a ZeroTier network and provide me the information about the ip adress of your OPC UA server? Or we agree on a fixed time on Monday when I will do the tests?
Hello good day.
I was doing tests yesterday with zero tier (1 computer with kepserver the other as a client), I managed to connect two PCs through zero tier but the client cannot connect to kepserver.
I think it's because of the DCOM settings.
I am going to try to configure the DCOMs and I will do tests, when I get an external connection to kepserver with zero tier I will let you know.
I will try to have everything by Monday and be able to tell you an hour.
Thanks a lot
okay
at 18:00 is perfect
I am from Spain and share the same schedule as Germany.
I do not have Teams but I will install it now and I will be connected at 18:00 pm
a greeting
The issue is solved and will be released today in realvirtual.io Professional 2021.10.